    Just wondering, Can 6/3 teck 90 cable be run on the surface of a dwelling unit and can it be buried without mechanical protection.
    Want to use it for a outdoor hot tub and it
    is easier to install than nmwu
    Appreciate any comments

    <font color="#a62a2a" size="1">[ September 29, 2002 11:27 PM: Message edited by: bigrockk ]</font>

  2. #2
    HB Forum Owner electric-ed's Avatar
    Join Date
    November 17th, 2001
    Posts
    191
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    TECK 90 is permitted for-
    1. exposed wiring where exposed to the weather, 2. direct earth burial (with protection as required by inspection authority). (Table 19)

    I would recommend a PVC sleeve where it emerges from the ground for mechanical protection, and follow Table 53 for burial depth.

    Hope this helps.

  3. #3
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Thanks for the reply E-ED
    Appreciate it